BarklieEstes
Member
- Location
- Richmond, VA
- Occupation
- Master Electrician
Good afternoon,
Does 690.47(A) require bringing detached structure grounding electrode system up to code when installing a solar system on it?
The situation at hand is a PV system installed on a boat dock roof that is connected to a boathouse subpanel (no electrode at the subpanel) that is fed by a 4-wire feeder from a single-family dwelling that has an existing grounding electrode system compliant with Article 250 Part III.
My perspective is that the PV system 1) is connected to associated distribution equipment connected to a ground electrode system, 2) the support structure utilizes an Article 250 Part III grounding electrode system (the one at the house), and 3) the PV array equipment grounding conductors are connected to that system in accordance with Part VII of Article 250.
I see that a 250.32(A) violation already exists. I don't see where Part II of Article 250 gets invoked or how a not-solidly grounded PV system contributes to that violation. In code terms, my argument would be that "the existing building is no less conforming to the provisions of the VCC than the existing building or structure was prior to the alteration."
Regards,
Barklie
Does 690.47(A) require bringing detached structure grounding electrode system up to code when installing a solar system on it?
The situation at hand is a PV system installed on a boat dock roof that is connected to a boathouse subpanel (no electrode at the subpanel) that is fed by a 4-wire feeder from a single-family dwelling that has an existing grounding electrode system compliant with Article 250 Part III.
My perspective is that the PV system 1) is connected to associated distribution equipment connected to a ground electrode system, 2) the support structure utilizes an Article 250 Part III grounding electrode system (the one at the house), and 3) the PV array equipment grounding conductors are connected to that system in accordance with Part VII of Article 250.
I see that a 250.32(A) violation already exists. I don't see where Part II of Article 250 gets invoked or how a not-solidly grounded PV system contributes to that violation. In code terms, my argument would be that "the existing building is no less conforming to the provisions of the VCC than the existing building or structure was prior to the alteration."
Regards,
Barklie