I working with Sokar Gridtie systems here.
The explaination on the links isn't too clear. they state that during the daytime you will have current from both the power company and from the solar array across the bus bar.
I would have to ask if this has been tested. If my array lets say 5KW 240 volt is generating full power at noon and lets say 10.6amp 15 amp breaker across the 2 hot bars. That power is first going to feed the devices in the house and any excess would be pushed out to the grid. The dependancy on the grid has been reduced. How can you have both unless you aren't generating enough from an array in the morning and in the evening. Even then you wouldn't have competing power sources for the bus bar.
The requirement is that on a "dwelling unit"
the sum of circuit breakers feeding current to a conductor or busbar
cannot exceed 120% of the rating of the busbar [NEC 690.64(B)(2)
Exception]. What this means is that on a typical 200A residential
service the maximum sum of breakers is 240A. If the main breaker for
the service panel is 200A that leave a maximum of 40A for for SMA Inverters

The explaination on the links isn't too clear. they state that during the daytime you will have current from both the power company and from the solar array across the bus bar.
I would have to ask if this has been tested. If my array lets say 5KW 240 volt is generating full power at noon and lets say 10.6amp 15 amp breaker across the 2 hot bars. That power is first going to feed the devices in the house and any excess would be pushed out to the grid. The dependancy on the grid has been reduced. How can you have both unless you aren't generating enough from an array in the morning and in the evening. Even then you wouldn't have competing power sources for the bus bar.
The requirement is that on a "dwelling unit"
the sum of circuit breakers feeding current to a conductor or busbar
cannot exceed 120% of the rating of the busbar [NEC 690.64(B)(2)
Exception]. What this means is that on a typical 200A residential
service the maximum sum of breakers is 240A. If the main breaker for
the service panel is 200A that leave a maximum of 40A for for SMA Inverters