donohuco
New member
- Location
- Oregon City, Oregon, USA
I just started a project where a small office building is utilizing a central emergency Inverter for egress illumination with the specs indicated below:
Inverter Spec: 120V 1PH 1.5 KVA MEYERS E-1150
Input: 120V, 1PH, 20A Branch Circuit
Output: 120V, 1PH, with (4) separate 20A branch Circuit Breakers.
I seem to see this setup / design a lot for commercial buildings where the inverter specified is between 1.5-5KVA. The input will be anywhere from a 20-50A s.p circuit breaker and the output will be 4-6 20A s.p circuit breakers.
I do not see how most smaller (1.5-5KVA) central emergency inverter designs like the ones above can meet selective coordination requirements. Can anyone let me know what i am mis-understanding on these.
Is selective coordination only required up to the input of the inverter?
Inverter Spec: 120V 1PH 1.5 KVA MEYERS E-1150
Input: 120V, 1PH, 20A Branch Circuit
Output: 120V, 1PH, with (4) separate 20A branch Circuit Breakers.
I seem to see this setup / design a lot for commercial buildings where the inverter specified is between 1.5-5KVA. The input will be anywhere from a 20-50A s.p circuit breaker and the output will be 4-6 20A s.p circuit breakers.
I do not see how most smaller (1.5-5KVA) central emergency inverter designs like the ones above can meet selective coordination requirements. Can anyone let me know what i am mis-understanding on these.
Is selective coordination only required up to the input of the inverter?