Do any of the loyal readers here have any experience using switchgear utilizing an auto throw-over scheme instead of a separate automatic transfer switch (ATS)?
For instance, say we have a main-tie-main arrangement where the second main is a gen-set. In this case, the tie breaker along with the two main breakers are controlled with PLC (and are integral to the gear), and they take the place of a separate ATS. How can this arrangement be said to meet the requirements of NEC 700.5 (D), which requires separate transfer 'equipment' for emergency loads?
Conversely, what would separate transfer 'equipment' that satisfies 700.5 (D) look like in this situation?
For instance, say we have a main-tie-main arrangement where the second main is a gen-set. In this case, the tie breaker along with the two main breakers are controlled with PLC (and are integral to the gear), and they take the place of a separate ATS. How can this arrangement be said to meet the requirements of NEC 700.5 (D), which requires separate transfer 'equipment' for emergency loads?