dahtective17
- Oregon
- Engineer
I'm reviewing a design for 600kW 480V portable generators being installed in a parking lot and connected to a building to allow parallel service with the existing utility connection to the building. The coupling between the utility and the generators is at a switchgear lineup outside of the building. There are many hoops and requirements that we are managing with the utility company to make this work, but an issue that I noticed is the contractor providing the generators would like to install 600V portable power cable on the asphalt/gravel between the generators and the switchgear. They would be installed for a period of 7 months before they will be removed.
How I'm reading NEC articles 400 and 590.4 (J), I don't see a way that it is permitted to route cables (even extra hard usage) on the ground like that. Am I missing something? I've seen it done before on generators, load banks, or other temp power solutions but I can't tell how the code permits it. NEC 2023 is in effect in this state.