(D) Size ? Equipment Bonding Jumper on Load Side of an
Overcurrent Device. The equipment bonding jumper on the
load side of an overcurrent device(s) shall be sized in accordance
with 250.122.
A single common continuous equipment bonding jumper
shall be permitted to connect two or more raceways or cables if
the bonding jumper is sized in accordance with 250.122 for the
largest overcurrent device supplying circuits therein.
250.102(E)(2)
(2) Outside a Raceway or an Enclosure. If installed on the
outside, the length of the bonding jumper or conductor or equipment
bonding jumper shall not exceed 1.8 m (6 ft) and shall be
routed with the raceway or enclosure.
250.102(E)(3)
(3) Protection. Bonding jumpers or conductors and equipment
bonding jumpers shall be installed in accordance with
250.64(A) and (B).
250.64(B)
(B) Securing and Protection Against Physical Damage.
Where exposed, a grounding electrode conductor or its
enclosure shall be securely fastened to the surface on which it
is carried. Grounding electrode conductors shall be permitted
to be installed on or through framing members. A 4 AWG or
larger copper or aluminum grounding electrode conductor shall
be protected if exposed to physical damage. A 6 AWG grounding
electrode conductor that is free from exposure to physical damage
shall be permitted to be run along the surface of the building
construction without metal covering or protection if it is securely
fastened to the construction; otherwise, it shall be protected in
rigid metal conduit RMC, intermediate metal conduit (IMC),
rigid polyvinyl chloride conduit (PVC), reinforced thermosetting
resin conduit (RTRC), electrical metallic tubing EMT, or cable
armor. Grounding electrode conductors smaller than 6 AWG
shall be protected in (RMC), IMC, PVC, RTRC, (EMT), or cable
armor. Grounding electrode conductors and grounding electrode
bonding jumpers shall not be required to comply with 300.5.