Re: NEC Art 700.1 & 700.6
I still disagree with Bob and caj. Per 700.6(D), transfer equipment shall supply only emergency loads. The handbook clarifies this and says the generator may serve non-emergency loads, but mulitple transfer switches are required. The transfer switch that serves emergency loads can not serve non-emergency loads.
Someone mentioned 700.5(A), but look at (B). That also requires a second transfer switch (how else would you do selective load shedding?).
Again, I think you should use commercial fixtures with battery backup for the required exit and egress lights (if that is cheaper than another transfer switch). Then the required multiple transfer switches are in the fixtures. Doors, radios, and everything else can go on the generator.
Someone also mentioned 517 as allowing one transfer switch for under 150KVA. But 517 also places limits on what can be put on this one transfer switch. Basically, only necessary items. Not just anything.
Steve