For applications < 600V....
Need clarification of this code section. Very confusing.
I was just at several jobsites and saw control transformers installed with a variety of scenarios with regards to overcurrent protection. This is very confusing. Let's just stick with the NEC (< 600V) - nevermind chicago code for now.
I saw a hot water boiler control panel with a control transformer where only the secondary was fused. The primary (3-phase 208) was NOT fused. It even confirmed it on the wiring diagram. No overcurrent protection on the primary side. I see similar scenarios all the time.
I also see hundreds of control transformers (typically 120/24V) under 100 VA, installed with NO primary overcurrent protection. I called (2) transformer companies and talked to their tech support people and both of them said they DO NOT provide primary side integral overcurrent protection on the transformers they make. Some modyels they offer are built with "secondary" overcurrent protection (via circuit breaker), but NO primary overcurrent protection. The tech support guys said, it's up to the contractor and the NEC code to determined if and when primary overcurrent protection is required. The way I interpret NEC 450.3 is that Primary overcurrent protection is "always" required for transformers. Yet, when I am on jobsites looking at installed transformers, in most cases there is NO overcurrent protection on the primary side. Why?
I have to make a presentation on this subject to our engineering staff and field electricians soon, and I'm trying to get to the bottom of this.
When is Primary overcurrent protection required for transformers and when is Secondary overcurrent protection required for transformers. Similarly, when is it NOT required? Again, were talking <600V, and in my case, small control transformers only (less than 500VA, typically with 24V secondaries)
:huh::slaphead:
Need clarification of this code section. Very confusing.
I was just at several jobsites and saw control transformers installed with a variety of scenarios with regards to overcurrent protection. This is very confusing. Let's just stick with the NEC (< 600V) - nevermind chicago code for now.
I saw a hot water boiler control panel with a control transformer where only the secondary was fused. The primary (3-phase 208) was NOT fused. It even confirmed it on the wiring diagram. No overcurrent protection on the primary side. I see similar scenarios all the time.
I also see hundreds of control transformers (typically 120/24V) under 100 VA, installed with NO primary overcurrent protection. I called (2) transformer companies and talked to their tech support people and both of them said they DO NOT provide primary side integral overcurrent protection on the transformers they make. Some modyels they offer are built with "secondary" overcurrent protection (via circuit breaker), but NO primary overcurrent protection. The tech support guys said, it's up to the contractor and the NEC code to determined if and when primary overcurrent protection is required. The way I interpret NEC 450.3 is that Primary overcurrent protection is "always" required for transformers. Yet, when I am on jobsites looking at installed transformers, in most cases there is NO overcurrent protection on the primary side. Why?
I have to make a presentation on this subject to our engineering staff and field electricians soon, and I'm trying to get to the bottom of this.
When is Primary overcurrent protection required for transformers and when is Secondary overcurrent protection required for transformers. Similarly, when is it NOT required? Again, were talking <600V, and in my case, small control transformers only (less than 500VA, typically with 24V secondaries)