NEC article addressing Romex fittings

Status
Not open for further replies.
Look on the article regarding NM cable. I'm pretty sure that early in the article there is a paragraph requiring fittings be listed.
 
What NEC article best addresses the requirement for listed connectors or fittings to protect type NM cable entering metal enclosures, especially appliances ?

Best thing I come up with is second sentence in 300.15:
"Fittings and connectors shall be used only with the specific wiring methods for which they are designed and listed."
 
Welcome to the forum.sounds like a test question.

334 deals with NM cable
And nothing in 334 directly answers OP question. That makes you go further back to more "general" articles such as 300 where I did find what I quoted, and 110, where you most likely come to conclusion you follow 110.3(B) and the answer is in product instructions more so than in NEC.
 