Hi all,
I was doing some calculations to get familiar with Ch.9 of NEC regarding conduit fill and found the following, if someone can help confirm that I did it right.
Q: 4#3 RHW and 1#8 RHW GND in PVC Sch 40, find the minimum size of PVC Sch 40.
Per Table C.11, 4#3 RHW can fit in 1-1/4''C PVC Sch 40. The problem is when you use Table 1, 4, & 5 to find the cross-section area of 1-1/4''C PVC Sch 40 for 40% fill is 0.581. But when you add up the cross-section area of the 4#3 RHW cables (Ignore the #8 ground wire and use the RHW without *) = 4 x 0.1521 = 0.6084 which is bigger than 0.581 (the cross-section area of 1-1/4''C PVC Sch 40). Does that mean Table C.11 is wrong on 4#3 RHW cables can fit in 1-1/4''C PVC Sch 40 conduit?
Thanks
I was doing some calculations to get familiar with Ch.9 of NEC regarding conduit fill and found the following, if someone can help confirm that I did it right.
Q: 4#3 RHW and 1#8 RHW GND in PVC Sch 40, find the minimum size of PVC Sch 40.
Per Table C.11, 4#3 RHW can fit in 1-1/4''C PVC Sch 40. The problem is when you use Table 1, 4, & 5 to find the cross-section area of 1-1/4''C PVC Sch 40 for 40% fill is 0.581. But when you add up the cross-section area of the 4#3 RHW cables (Ignore the #8 ground wire and use the RHW without *) = 4 x 0.1521 = 0.6084 which is bigger than 0.581 (the cross-section area of 1-1/4''C PVC Sch 40). Does that mean Table C.11 is wrong on 4#3 RHW cables can fit in 1-1/4''C PVC Sch 40 conduit?
Thanks