NEC Ch.9 Table C.11 Error?

Yeah, I was referring to the RHW with outer covering.

I didn't know the rounding note existed. So per the note, you would round up the number you got from (conduit fill area / total cable cross-section area of same conductors). So there is nothing wrong with the table for the 4#3 RHW.

Looking at the notes, this rounding only applies when you size conductor of same size and not a mix of different size conductors.

Thank you everyone for the feedback.
I disagree. The round up is under any circumstances not just when all conductors are the same. Tables in Appendix C are only for conductors that are the same
 
I take mistakes in the table personally.

I spent many hours re-working the tables in Appendix C because there was at least one error found. When I present NFPA with the error they decided to use the tables I made instead of the existing ones. The tables I did included all the conductors available, whereas the old table did not.

Every time someone says they found an error my heart stops. I figured I had screwed up. So far that hasn't been the case. I keep my fingers crossed. haha

There still may be some especially if the wire sizes in Table 5 are not correct.. I did not measure the wires.
 
I take mistakes in the table personally.

I spent many hours re-working the tables in Appendix C because there was at least one error found. When I present NFPA with the error they decided to use the tables I made instead of the existing ones. The tables I did included all the conductors available, whereas the old table did not.

Every time someone says they found an error my heart stops. I figured I had screwed up. So far that hasn't been the case. I keep my fingers crossed. haha

There still may be some especially if the wire sizes in Table 5 are not correct.. I did not measure the wires.
WOW you really checked every table? What code cycle did they adopt your tables?
 
I disagree. The round up is under any circumstances not just when all conductors are the same. Tables in Appendix C are only for conductors that are the same
2020 NEC Chapter 9 Table 1 Note 7 starts off "When calculating the maximum number of conductors or cables permitted in a conduit or tubing, all of the same size (total cross-sectional area including insulation), . . ." So the allowance only applies when all the conductors or cables are the same size.

Cheers, Wayne
 
WOW you really checked every table? What code cycle did they adopt your tables?

It may have been the 2017. Before that I was at a meeting in Raleigh, NC and I brought it up to the CMP members that were there. They disagreed with me and said it was probably a rounding up problem. I insisted there was a problem, in fact, I sent in the question ahead of time with an example. He finally said to feel free to re-work the tables. His way of saying--bug off.

So I set up some crazy spreadsheets with some formulas that went on forever. Like the one below. Someone with more smarts than I could probably have simplified it. I created tables and heck I can't even remember what I did but it worked

=IF(VLOOKUP(C$9,EMT!$A$10:$N$25,14,FALSE)/VLOOKUP($B49,Table5NEC!$B49:$F49,5,FALSE)>=2.8,ROUND(VLOOKUP(C$9,EMT!$A$10:$N$25,14,FALSE)/VLOOKUP($B49,Table5NEC!$B49:$F49,5,FALSE)-0.3,0),IF(OR(VLOOKUP(C$9,EMT!$A$10:$N$25,12,FALSE)/VLOOKUP($B49,Table5NEC!$B49:$F49,5,FALSE)>=2.8,VLOOKUP(C$9,EMT!$A$10:$N$25,12,FALSE)/VLOOKUP($B49,Table5NEC!$B49:$F49,5,FALSE)>=1.8),2,IF(VLOOKUP(C$9,EMT!$A$10:$N$25,10,FALSE)/VLOOKUP($B49,Table5NEC!$B49:$F49,5,FALSE)>=0.8,1,0)))

After I did all the work I had the same problem.....damn

I figured the one common element was the wire thickness. And that was the issue they had transpose the insulation numbers, in one spot., for something like the and thwn. I don't remember the exact insulation type.

Anyway, I told them the issue and said if they wanted my tables here they are.... I didn't expect anything since I was past the deadline. I was surprised when I got the code book I say my tables.
 
2020 NEC Chapter 9 Table 1 Note 7 starts off "When calculating the maximum number of conductors or cables permitted in a conduit or tubing, all of the same size (total cross-sectional area including insulation), . . ." So the allowance only applies when all the conductors or cables are the same size.

Cheers, Wayne

I read right past that. Thanks
 