WOW you really checked every table? What code cycle did they adopt your tables?
It may have been the 2017. Before that I was at a meeting in Raleigh, NC and I brought it up to the CMP members that were there. They disagreed with me and said it was probably a rounding up problem. I insisted there was a problem, in fact, I sent in the question ahead of time with an example. He finally said to feel free to re-work the tables. His way of saying--bug off.
So I set up some crazy spreadsheets with some formulas that went on forever. Like the one below. Someone with more smarts than I could probably have simplified it. I created tables and heck I can't even remember what I did but it worked
=IF(VLOOKUP(C$9,EMT!$A$10:$N$25,14,FALSE)/VLOOKUP($B49,Table5NEC!$B49:$F49,5,FALSE)>=2.8,ROUND(VLOOKUP(C$9,EMT!$A$10:$N$25,14,FALSE)/VLOOKUP($B49,Table5NEC!$B49:$F49,5,FALSE)-0.3,0),IF(OR(VLOOKUP(C$9,EMT!$A$10:$N$25,12,FALSE)/VLOOKUP($B49,Table5NEC!$B49:$F49,5,FALSE)>=2.8,VLOOKUP(C$9,EMT!$A$10:$N$25,12,FALSE)/VLOOKUP($B49,Table5NEC!$B49:$F49,5,FALSE)>=1.8),2,IF(VLOOKUP(C$9,EMT!$A$10:$N$25,10,FALSE)/VLOOKUP($B49,Table5NEC!$B49:$F49,5,FALSE)>=0.8,1,0)))
After I did all the work I had the same problem.....damn
I figured the one common element was the wire thickness. And that was the issue they had transpose the insulation numbers, in one spot., for something like the and thwn. I don't remember the exact insulation type.
Anyway, I told them the issue and said if they wanted my tables here they are.... I didn't expect anything since I was past the deadline. I was surprised when I got the code book I say my tables.