it says in a book about NEC "The rating of the branch circuit is determined by the size of the
overcurrent protection device. An individual receptacle on a single branch
circuit cannot have an amperage that is less than the rating of the OCPD,
as specified in NEC Article 210.21(B"
so isnt it false? you have a 20 A receptacle and the circuit is 15 A so you cant operate ur device
am i wrong?
	
		
			
		
		
	
				