Re: NEC - Communication Cables - 360 degrees?
90.3 Code Arrangement.
This Code is divided into the introduction and nine chapters, as shown in Figure 90.3. Chapters 1, 2, 3, and 4 apply generally; Chapters 5, 6, and 7 apply to special occupancies, special equipment, or other special conditions. These latter chapters supplement or modify the general rules. Chapters 1 through 4 apply except as amended by Chapters 5, 6, and 7 for the particular conditions.
Chapter 8 covers communications systems and is not subject to the requirements of Chapters 1 through 7 except where the requirements are specifically referenced in Chapter 8.
Unless Chapter 8 references a requirement else where there is no requirment.
800.6 references 300.4(D), which is for protection of cables.
BICSI standards are the best source for information. This is a performance issue, not NEC.
But typically no more than 180 deg and about 100 ft between pull points, no more than 25 lbs pulling tension.