Re: NEC Compliant..?
The full load amp rating of the filter is not suffcient to determine it's suitability. You must also know what fault current rating it has as well as the available fault current where the it is being mounted.
Because your filter has a 20A rating, it sounds like it is wired in series rather than in parallel with the load. As Al noted, physically installing this in the panel may not be possible.