Is the below correct?
320amp (400amp max) Meter Center Application
Lets say I have 350amps load on my 400amp MDP.
200amp continuous loads
150amp non-continuous loads
Will the 320amp meter center/socket be a correct application? My understanding as long as the continuous load is 320 or less and the combined loads (non + continuous) is 400amps or less, the 320amp meter will be fine.
Cheers