Re: NEC definition of Low Voltage
The mother of all low volage articles is Art 725, but the title is Class 1, Class 2, and Class 3 Remote-Control, Signaling, and Power-Limited Circuits. The nec does not use the term low voltage. Circuits in Art 725 per the FPN are:
FPN: The circuits described herein are characterized by usage and electrical power limitations that differentiate them from electric light and power circuits; therefore, alternative requirements to those of Chapters 1 through 4 are given with regard to minimum wire sizes, derating factors, overcurrent protection, insulation requirements, and wiring methods and materials.
Once a circuit exceeds the limits in Art 725 it becomes a fire hazard or shock hazard and is wired per the rules in Chapter 3. For example a 1,000 VA 12 v transformer for landscape lighting could be low voltage, but not limited energy, as it could cause a fire. A car battery is low voltage but there is enoght energy that they can and have started fires.
Also 30 volts is often considered the voltage below which no protection is required.