Ran into an interesting contradiction while sizing conduit.
Situation: 3 conductors of 300kcm each in EMT w/o a grounding conductor. Each conductor (THWN) has an area of .4608 square inches. The total area for all three is then 1.3824 Sq in.
If you plug that total into the table for EMT in chapter 9, you find 2.5" EMT is required at 40% fill. However, if you check in Annex C (as all the wires are the same size) It allows 3 conductors in 2" EMT, altho the combined area clearly exceeds the limit for 40% fill.
Obviously I would choose to err on the side of the larger conduit, for a variety of reasons (cost not being one of them) but I found the conflicting information interesting.
Thoughts?