reyamkram
- Hanover park, il
Switched box looks like a DC motor drive to me.What are we looking at? Two cords fed from one cap? What's with the switched box?
Are the following attached pictures installed properly according to the NEC? If not, where in the NEC would I find the facts so I can bring it to my superiors attention.
Thanks,
reyamkram
It looks like commercial-kitchen equipment.
The NEC basically stops at the receptacle.
I agree on the first one, I seriously doubt that ANY cord cap is listed for more than one conductor and in addition, there will be a maximum SIZE of conductor that it can handle, so two conductors would likely exceed that.If the install falls under the NEC in both cases are likely a violation of 110,3(B). You would need to check the manufacturers technical data to see if either item was listed for that use. Doubtful either is acceptable.
If , as suggested, it is part of equipment wriing then it goes back to the listing on the equipment.
On the second one, the DC drive itself appears to be NEMA 1, so the cord grip used on the cable coming out of it would be fine if listed for CORD. That APPEARS to be a cable clamp for NM or MC cable however, so if it is, then that too would be a 110.3.B violation.
It looks like there are two cords in the connector, a yellow one and a black one. I know of no cord grip suitable for more than one cord.