He is referring to the following example from Annex D:
Example D1(a) One-Family Dwelling
The dwelling has a floor area of 1500 ft2, exclusive of an unfinished cellar
not adaptable for future use, unfinished attic, and open porches. Appliances
are a 12-kW range and a 5.5-kW, 240-V dryer. Assume range and
dryer kW ratings equivalent to kVA ratings in accordance with 220.54 and
220.55.
...detailed calcs follow with results used in example b
Example D1(b) One-Family Dwelling
Assume same conditions as Example No. D1(a), plus addition of one 6-A,
230-V, room air-conditioning unit and one 12-A, 115-V, room airconditioning
unit,* one 8-A, 115-V, rated waste disposer, and one 10-A,
120-V, rated dishwasher. See Article 430 for general motors and Article
440, Part VII, for air-conditioning equipment. Motors have nameplate
ratings of 115 V and 230 V for use on 120-V and 240-V nominal voltage
systems.
*(For feeder neutral, use larger of the two appliances for unbalance.)
From Example D1(a), feeder current is 78 A (3-wire, 240 V).
Line A, Neutral, Line B
Amperes from Example D1(a) = 78, 61, 78
One 230-V air conditioner = 6, —, 6
One 115-V air conditioner and 120-V dishwasher = 12, 12, 10
One 115-V disposer = —, 8, 8
25% of largest motor (see 430.24) = 3, 3, 2
Total amperes per line = 99, 84, 104
Therefore, the service would be rated 110 A.
es1451
The example has already detailed the calculations. What specifically are you having trouble with?