nec feeder ampacity vs panel bus rating

Status
Not open for further replies.
C3PO said:
As long as the bus rating is greater than or equal to the feeder size you are ok.

As long as the panel bus rating is greater than or equal to the feeder overcurrent protective device setting/rating you are ok.
 
jim dungar said:
As long as the panel bus rating is greater than or equal to the feeder overcurrent protective device setting/rating you are ok.

That is what I meant :smile:
 
steve blackmon said:
I understood from my last code update seminar that now the feeder size to a panel must match the bus rating of the panel? am I wrong?

What code article/section was being discussed ?
 
C3PO said:
That is what I meant :smile:

I was positive you did.:smile:

I have been watching too many conventions on TV and I am getting gun-shy about "sound bites" being used out of context.
 
A few years ago I did a load calculation and ended up deciding that a 800A breaker was the answer (I think the calculated load was like 610 amps).

The electrician hooked up the machine to a 400A feeder. It actually never pulled much more than 300 amps.
 