Charlie: Excellent response.
I have traced the history of the separately derived system back to its origin, in 1914. The definition has never been changed for an AC system.
In the beginning, the term was "isolated system".
This was a premises supplied by a light plant, or generator. Some of the light plants operated at 24 volts, and were not grounded. The 120/240 volt generators were not grounded until 1914.
The term "isolated system" changed to "AC systems without external connections" in the 1930's. This was during the REA era, where rural farms were being electrified. Most of the farms were separately derived systems, powered by a generator, and ungrounded.
The utility companies would not connect to these "separately derived systems" until they were grounded. The section in 250 was created to illustrate the method for grounding the separately derived system.
The term "AC systems without external connections" changed to "Separately derived systems" in 1956.
This change was for editing purposes, by a staff member, for reasons of being more correct technically.
According to the curator of archives at NFPA headquarters.
There has never been any submittals for changing the definition of a separately derived system. The definition has changed by individuals applying their personal spin, and fabricating the purpose of a separately derived system without being aware of the true definition.
This incorrect perception is creating two ground points on a premises wiring system.
Just ask yourself...Why call a generator, or transformer, a separately derived system? Call them what they are.
By grounding a transformer under the instructions of 250.30 for a separately derived system, a ground loop is created. In many cases this is a second ground electrode system on the same premises. This is a hazard, and affects sensitive equipment.
The current flow, in the equipment ground conductor to the ground point of the transformer is common mode. The same net difference will appear on the service conductors.
The grounding method for a "separately derived system" is referring to the premises wiring system, not the source of power.
A generator, properly connected, will not interfere with the operation of GFI protection, as indicated in the handbooks. Disconnecting the utility neutral has nothing to do with GFI protection. Again, a fabricated explanation.
[ July 07, 2003, 11:58 AM: Message edited by: bennie ]
Charlie: Excellent response.
I have traced the history of the separately derived system back to its origin, in 1914. The definition has never been changed for an AC system.
In the beginning, the term was "isolated system".
This was a premises supplied by a light plant, or generator. Some of the light plants operated at 24 volts, and were not grounded. The 120/240 volt generators were not grounded until 1914.
The term "isolated system" changed to "AC systems without external connections" in the 1930's. This was during the REA era, where rural farms were being electrified. Most of the farms were separately derived systems, powered by a generator, and ungrounded.
The utility companies would not connect to these "separately derived systems" until they were grounded. The section in 250 was created to illustrate the method for grounding the separately derived system.
The term "AC systems without external connections" changed to "Separately derived systems" in 1956.
This change was for editing purposes, by a staff member, for reasons of being more correct technically.
According to the curator of archives at NFPA headquarters.
There has never been any submittals for changing the definition of a separately derived system. The definition has changed by individuals applying their personal spin, and fabricating the purpose of a separately derived system without being aware of the true definition.
This incorrect perception is creating two ground points on a premises wiring system.
Just ask yourself...Why call a generator, or transformer, a separately derived system? Call them what they are.
By grounding a transformer under the instructions of 250.30 for a separately derived system, a ground loop is created. In many cases this is a second ground electrode system on the same premises. This is a hazard, and affects sensitive equipment.
The current flow, in the equipment ground conductor to the ground point of the transformer is common mode. The same net difference will appear on the service conductors.
The grounding method for a "separately derived system" is referring to the premises wiring system, not the source of power.
A generator, properly connected, will not interfere with the operation of GFI protection, as indicated in the handbooks. Disconnecting the utility neutral has nothing to do with GFI protection. Again, a fabricated explanation.