Kartracer087
Member
- Location
- Chicago
- Occupation
- Consulting Engineer
I am writing to ask why do the majority of the calculations that I have seen for multifamily dwellings do not take into account 230.42 (A) 1 and 2 when sizing the service entrance conductors:
(A) General. The ampacity of the service-entrance conductors
before the application of any adjustment or correction
factors shall not be less than either (A)(1) or (A)(2).
Loads shall be determined in accordance with Part III, IV,
or V of Article 220, as applicable. Ampacity shall be determined
from 310.15. The maximum allowable current of
busways shall be that value for which the busway has been
listed or labeled.
(1) The sum of the noncontinuous loads plus 125 percent
of continuous loads
(2) The sum of the noncontinuous load plus the continuous
load if the service-entrance conductors terminate in an
overcurrent device where both the overcurrent device
and its assembly are listed for operation at 100 percent
of their rating
Most of the time you see the selection of the service entrance cable be based directly on your article 220 load calculations, but I never see the noncontinuous/continuous load factors applied to this calculation like you would have to per 230.42 (A) 1. I would just assume the worst case scenario would be you take your demand load from article 220 and multiply it by 1.25, but I've never ever seen it done this way... Is there some reason why you don't have to do it like that?
Thanks.
(A) General. The ampacity of the service-entrance conductors
before the application of any adjustment or correction
factors shall not be less than either (A)(1) or (A)(2).
Loads shall be determined in accordance with Part III, IV,
or V of Article 220, as applicable. Ampacity shall be determined
from 310.15. The maximum allowable current of
busways shall be that value for which the busway has been
listed or labeled.
(1) The sum of the noncontinuous loads plus 125 percent
of continuous loads
(2) The sum of the noncontinuous load plus the continuous
load if the service-entrance conductors terminate in an
overcurrent device where both the overcurrent device
and its assembly are listed for operation at 100 percent
of their rating
Most of the time you see the selection of the service entrance cable be based directly on your article 220 load calculations, but I never see the noncontinuous/continuous load factors applied to this calculation like you would have to per 230.42 (A) 1. I would just assume the worst case scenario would be you take your demand load from article 220 and multiply it by 1.25, but I've never ever seen it done this way... Is there some reason why you don't have to do it like that?