The knowledge contained in this forum is priceless so I wanted to get your opinions on a code question.
We always separate our 120 and above AC components from our 24 VDC components by putting them in separate panels. The AC side is always interlocked, in compliance with NFPA79 6.2.3.1. The 24 VDC panel is not interlocked, which is great for PLC/network/controls access.
Many of our machines use PCs. We'd like to keep them in a panel to protect them from environment but still have them accessible. The problem is that the PCs run at 120VAC of course, and would require a 120 receptacle in the 24VDC panel or power to run over from the AC panel.
My reading says that any live parts above 50VAC or 60VDC has to be interlocked per NFPA 79 and that adding a receptacle or even running power over to the PCs internal power supply qualifies as "live parts" above 50VAC and therefore is not doable, even if common sense says a 120 receptacle poses very little danger.
Recently it has been suggested that it would be OK to put the PCs in there because we would have a "disconnecting means" (receptacle) kosher with NFPA 79 and there would be no exposed conductors meeting NFPA 70E Electrically safe work conditions requirements.
This is one of those weird spots where common sense and code are at odds. What do you think? Thanks for reading.
We always separate our 120 and above AC components from our 24 VDC components by putting them in separate panels. The AC side is always interlocked, in compliance with NFPA79 6.2.3.1. The 24 VDC panel is not interlocked, which is great for PLC/network/controls access.
Many of our machines use PCs. We'd like to keep them in a panel to protect them from environment but still have them accessible. The problem is that the PCs run at 120VAC of course, and would require a 120 receptacle in the 24VDC panel or power to run over from the AC panel.
My reading says that any live parts above 50VAC or 60VDC has to be interlocked per NFPA 79 and that adding a receptacle or even running power over to the PCs internal power supply qualifies as "live parts" above 50VAC and therefore is not doable, even if common sense says a 120 receptacle poses very little danger.
Recently it has been suggested that it would be OK to put the PCs in there because we would have a "disconnecting means" (receptacle) kosher with NFPA 79 and there would be no exposed conductors meeting NFPA 70E Electrically safe work conditions requirements.
This is one of those weird spots where common sense and code are at odds. What do you think? Thanks for reading.