Is this a true mostly enclosed room? Like a screened in enclosure, or is it a true out of doors, and exposed to the weather?
If it is truly on the outside of main structure and exposed to weather 210.8 requirements would be involved regardless of proximity to the sink. However regarding 210.12 requirements to insist on AFCI on the outside receptacles can be argued not required on exterior of building. From my thinking if the space falls into requiring GFCI as a result of being exposed to weather it is not a room that requires AFCI. I would however suggest that installation of adequate receptacles for countertops use in food/ drink preparation just from a practical point of view.
If it is truly on the outside of main structure and exposed to weather 210.8 requirements would be involved regardless of proximity to the sink. However regarding 210.12 requirements to insist on AFCI on the outside receptacles can be argued not required on exterior of building. From my thinking if the space falls into requiring GFCI as a result of being exposed to weather it is not a room that requires AFCI. I would however suggest that installation of adequate receptacles for countertops use in food/ drink preparation just from a practical point of view.