hurk27
- Portage, Indiana NEC: 2008
Re: NEC Questions
electrofelon:
It won't! A ground rod does not provide a low enough impedance path to return enough current back to the transformer to provide this protection period! A ground rod that has a impedance of 25 ohms at 120 volts would only allow 4.8 amps to flow back to the transformer. If the service has a unbalance current higher than this you will still have voltage fluctuation and will still damage equipment. This also goes for the thinking that a ground rod will open a breaker. As before only if the breaker has a rating lower than the 4.8 amps ! Most dwellings can have very unbalanced panels because of the load diversities. And many times can have much more current on the neutral than the 4.8 amps a ground rod could provide.
The NEC only requires ground rods for lightning, line surges, unintentional contact with higher-voltage lines, or to stabilize the voltage to earth during normal operation period!!!
Just as it says in 250.4(A)(1):
electrofelon:
Do you think the ground rod will protect against the lost neutral?What happens when the neutral between the service disconnect and utility is compromised?
(1) Electrical System Grounding. Electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to earth during normal operation.