hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
Re: NEC Questions
electrofelon:
It won't! A ground rod does not provide a low enough impedance path to return enough current back to the transformer to provide this protection period! A ground rod that has a impedance of 25 ohms at 120 volts would only allow 4.8 amps to flow back to the transformer. If the service has a unbalance current higher than this you will still have voltage fluctuation and will still damage equipment. This also goes for the thinking that a ground rod will open a breaker. As before only if the breaker has a rating lower than the 4.8 amps ! Most dwellings can have very unbalanced panels because of the load diversities. And many times can have much more current on the neutral than the 4.8 amps a ground rod could provide.
The NEC only requires ground rods for lightning, line surges, unintentional contact with higher-voltage lines, or to stabilize the voltage to earth during normal operation period!!!
Just as it says in 250.4(A)(1):
electrofelon:
Do you think the ground rod will protect against the lost neutral?What happens when the neutral between the service disconnect and utility is compromised?
It won't! A ground rod does not provide a low enough impedance path to return enough current back to the transformer to provide this protection period! A ground rod that has a impedance of 25 ohms at 120 volts would only allow 4.8 amps to flow back to the transformer. If the service has a unbalance current higher than this you will still have voltage fluctuation and will still damage equipment. This also goes for the thinking that a ground rod will open a breaker. As before only if the breaker has a rating lower than the 4.8 amps ! Most dwellings can have very unbalanced panels because of the load diversities. And many times can have much more current on the neutral than the 4.8 amps a ground rod could provide.
The NEC only requires ground rods for lightning, line surges, unintentional contact with higher-voltage lines, or to stabilize the voltage to earth during normal operation period!!!
Just as it says in 250.4(A)(1):
(1) Electrical System Grounding. Electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to earth during normal operation.