kwired
Electron manager
- NE Nebraska
- EC
I don't have a copy of the 2014 so I'm going solely on the pasted section Infinity posted.
I don't see the language that 310.15(B)(6) [2008 code] had concerning the service or feeder serving the entire load. Or as it put it, "serves as the main power feeder"
I guess I'm asking if that language is necessary since if you have a subpanel the 83% could be used but based only on the service size? Or the language may be there and I can't see it because I don't have the actual code to read.
It is (B)(7) in 2011 and 2014 - but I think it was changed in 2011 and was (B)(6) in 2008. Anyway, here is all of (B)(7) from 2014. There is no more table, just the 83%, and some details to go with it, and the fact there is no table with specific values makes it easier to determine that they intend to make adjustments for number of conductors in raceway or ambient temp. Some say we had to do that before - but was not really all that clear just how to do so, now you are doing same thing you do with any other conductor just with a final result that is otherwise 83% of the usual method. This is also mentioned in informational note1.
This means for a 100 amp service, conductors are selected just like they normally are for other applications, but instead of needing a final ampacity of 100 amps it only needs to be 83 amps if they are conductors that supply the entire dwelling unit load.
I bolded some key items that seem to get asked about frequently here on the forum when talking about this section.
(7) 120/240-Volt, Single-Phase Dwelling Services and Feeders.
For one-family dwellings and the individual dwelling units of two-family and multifamily dwellings, service and feeder conductors supplied by a single-phase, 120/240-volt system shall be permitted be sized in accordance with 310.15(B)(7)(1) through (4).
For a service rated 100 through 400 A, the service conductors supplying the entire load associated with a one-family dwelling, or the service conductors supplying the entire load associated with an individual dwelling unit in a two-family or multifamily dwelling, shall be permitted to have an ampacity not less than 83 percent of the service rating.
For a feeder rated 100 through 400 A, the feeder conductors supplying the entire load associated with a onefamily dwelling, or the feeder conductors supplying the entire load associated with an individual dwelling, unit in a two-family or multifamily dwelling, shall be permitted to have an ampacity not less than 83 percent of the feeder rating.
In no case shall a feeder for an individual dwelling unit be required to have an ampacity greater than that specified in 310.15(B)(7)(1) or (2).
Grounded conductors shall be permitted to be sized smaller than the ungrounded conductors, provided that the requirements of 220.61 and 230.42 for service conductors or the requirements of 215.2 and 220.61 for feeder conductors are met.
Informational Note No. 1: The conductor ampacity may require other correction or adjustment factors applicable to the conductor installation.
Informational Note No. 2: See Example D7 in Annex D.
Format or links/special characters (because it was copied from E-book version of NEC) may have not copied exactly as printed in hard copy NEC, but main content is still there AFAIK.