What would prevent me from identifing all my 120/208 ungrounded conductors as black and all my 277/480 ungrounded conductors as red?
210.5(C) if you're on the 2008 NEC.
What would prevent me from identifing all my 120/208 ungrounded conductors as black and all my 277/480 ungrounded conductors as red?
210.5(C) if you're on the 2008 NEC.
YES
(C) Ungrounded Conductors. Where the premises wiring system has branch circuits supplied from more than one nominal voltage system, each ungrounded conductor of a branch circuit shall be identified by phase or line and system at all termination, connection, and splice points. The means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means. The method utilized for conductors originating within each branch-circuit panelboard or similar branch-circuit distribution equipment shall be documented in a manner that is readily available or shall be permanently posted at each branch-circuit panelboard or similar branch-circuit distribution equipment.
I missed by phase meaning A, B, C need to have different colors for both systems
You could still run all blacks for your low voltage and all reds for your high voltage, but you'd have to mark them somehow at all terminations, connections, splices etc.
210.5(C) if you're on the 2008 NEC.
What would prevent me from identifing all my 120/208 ungrounded conductors as black and all my 277/480 ungrounded conductors as red?
Its interesting there are far more questions on this color code than on the re-identification of 6 and smaller neutrals and EGC with phase tape. Every electrician has violated 200.6 and 250.119.
If all/most electricians use the standard black,red, blue for 120/208v and brown, orange, yellow for 277/480v, why does the NEC remain silent? :-?
Because it is a design issue and not a code issue.
I try to be in the "If it ain't broke don't fix it" school of thought. I learned the trade standard color-coding within the first few weeks of my first term of apprenticeship, and it's stuck ever since. Same with every other electrician I've worked with. We all know the color coding, and it's been convention for so long that there's probably no real problems being caused by it, so there's probably no real benefit to "officializing" it in the code. Same reason why equipment grounding conductors are still called equipment grounding conductors.
Yet 'officially', gray can be an ungrounded or a grounded.![]()
Only in installations prior to the 02 cycle.
Roger
To clarify, up through the 1999, gray was officially an ungrounded color...