AC_DC

Member
Location
San Gabriel
Hi,

I am trying to calculate voltage drop using the formula: VD=L*R*I/1000 where R values can be found from NEC table 9. However, that table 9 is for three single conductor in conduit. What if I have more than 3 conductors in conduit, where I can find the adjustment factor or how can I calculate for more than 3 single conductors in conduit?
 

shoaib10

Member
Location
DC
I dont know if this is correct but what i may do is as per 310.15(B)(3)(a) to do the adjustment factor and then get the corresponding ampacity and look it up in table 310.15(B)(16) to get the wire size...From that you can look up in Chapter 9 table 9 for AC resistance of the cable....
 

AC_DC

Member
Location
San Gabriel
NEC Table9

NEC Table9

My question is that after I calculate ampacity using Table310.15(B)(3)(a), then Table 310.15(B)(16), I know which wire I need to use. Since my length of wire is long, I am considering there is voltage drop. I am using VD=L*R*I/1000 where R values are from Table9 in NEC. However, that table 9 on NEC says Three-Single-Conductors in Conduit. But I have 7conductors in my conduit. Is it okay to use my R value from table9 even though I have more than 3 conductors in my conduit.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
The NEC is not a design manual. :)

I would use an online voltage drop calculator.

Same here, but if you look up what 'R' means in VD=L*R*I/1000, it specifies that 'R' be taken from the NEC.

I did run across this, though.

Wire resistance calculations

The n gauge wire resistance R in ohms per kilofeet (Ω/kft) is equal to 0.3048×1000000000 times the wire's resistivity ρ in ohm-meters (Ω·m) divided by 25.42 times the cross sectional area An in square inches (in2):
Rn (Ω/kft) = 0.3048 × 109 × ρ(Ω·m) / (25.42 × An (in)
)
The n gauge wire resistance R in ohms per kilometer (Ω/km) is equal to 1000000000 times the wire's resistivity ρ in ohm-meters (Ω·m) divided by the cross sectional area An in square millimeters (mm2):
Rn (Ω/km) = 109 × ρ(Ω·m) / An (mm
)



For copper, ρ = 1.68×10−8 Ω per meter
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
What is “K” in the formulas? K is the “electrical resistivity” of the type of conductor being used. The K value isa constant and can be found in most physics tables that provide resistivity of variousmaterials. This electrical resistivity is calculated by (electrical resistance x cross-sectionalarea/ longitudinal length) and is expressed as (ohms x cmil/ft) or simply (ohms-cmil/ft.) Copper has a K value of 12.9 ohms-cmil/ft and aluminum has a K value of21.2 ohms-cmil/ft. Other reference materials may show slightly different values, but for thepurposes of this discussion, these values are acceptable. These two values are derivedfrom the data found in Chapter 9, Table 8 of the Code. The K factor is found by multiplyingthe conductor’s resistance (ohm/kFT) by the conductor’s circular mil area and then dividingby 1000.

http://www.adamselectric.coop/wp-content/uploads/2015/02/Voltage-Drop.pdf
 

Smart $

Esteemed Member
Location
Ohio
.... But I have 7conductors in my conduit. Is it okay to use my R value from table9 even though I have more than 3 conductors in my conduit.
Don't know of any online calculator offhand that compensates for the number of conductors. Anyone?

There are two scenarios in derating for the number of conductors. You either upsize the conductor to maintain a specific ampacity... or you do not upsize because the derated ampacity is sufficient. In either scenario, the derating is to ensure the conductors do not exceed a certain temperature. That temperature is 75°C. It is also the temperature at which the R value in Table 9 is established (see title)... so the crux of this paragraph is, sure, by all means, use your value from Table 9.
:angel:
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Don't know of any online calculator offhand that compensates for the number of conductors. Anyone?

That's the crux of the biscuit. Table 9 is for a combination of resistance and reactance specifically for 3 phase, 3 conductors per conduit. The reactance will change if the number of conductors per conduit changes, but there is no adjustment factors in the table. Table 8 is for DC, resistance only, and the amount of conductors per conduit doesn't matter. Why the VD formula the OP posted doesn't take that into consideration is puzzling.
 

Carultch

Senior Member
Location
Massachusetts
In either scenario, the derating is to ensure the conductors do not exceed a certain temperature. That temperature is 75°C. It is also the temperature at which the R value in Table 9 is established (see title)... so the crux of this paragraph is, sure, by all means, use your value from Table 9.
:angel:

:thumbsup:
 

shoaib10

Member
Location
DC
Don't know of any online calculator offhand that compensates for the number of conductors. Anyone?

There are two scenarios in derating for the number of conductors. You either upsize the conductor to maintain a specific ampacity... or you do not upsize because the derated ampacity is sufficient. In either scenario, the derating is to ensure the conductors do not exceed a certain temperature. That temperature is 75°C. It is also the temperature at which the R value in Table 9 is established (see title)... so the crux of this paragraph is, sure, by all means, use your value from Table 9.
:angel:

I am just trying to understand..So first he has to derate using table 310.15(B)(3)(a) to do the adjustment factor and then get the corresponding ampacity and look it up in table 310.15(B)(16) to get the wire size...From that you can look up in Chapter 9 table 9 for AC resistance of the cable....Am i right?
 

Smart $

Esteemed Member
Location
Ohio
I am just trying to understand..So first he has to derate using table 310.15(B)(3)(a) to do the adjustment factor and then get the corresponding ampacity and look it up in table 310.15(B)(16) to get the wire size...From that you can look up in Chapter 9 table 9 for AC resistance of the cable....Am i right?
That's certainly part of a well-designed, compliant installation. :D
 

Ingenieur

Senior Member
Location
Earth
That's the crux of the biscuit. Table 9 is for a combination of resistance and reactance specifically for 3 phase, 3 conductors per conduit. The reactance will change if the number of conductors per conduit changes, but there is no adjustment factors in the table. Table 8 is for DC, resistance only, and the amount of conductors per conduit doesn't matter. Why the VD formula the OP posted doesn't take that into consideration is puzzling.

how much will it change?
the magnetic field for 3 x 100 A and 6 x 50 A are the same for a closed loop (conduit) Amperes Law
in the case of balanced 3 ph most cancels anyways
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
how much will it change?
the magnetic field for 3 x 100 A and 6 x 50 A are the same for a closed loop (conduit) Amperes Law
in the case of balanced 3 ph most cancels anyways

That's not the point. The point, at least to me, is the verbiage used. I'll use an online calculator and call it a day. The question was about the formula in post #1. Not real life. And someone thinks it matters, or it wouldn't be explicit as to 'three phase, three wires'. Why not just call it 60 Hz AC if it doesn't matter?
 