Okay..Took me some time to get it..But finally..:thumbsup:
Yeah, that was a good one. Glad you are being a sport about it and you didn't see me snicker the first time I read it. :lol:
Okay..Took me some time to get it..But finally..:thumbsup:
That's not the point. The point, at least to me, is the verbiage used. I'll use an online calculator and call it a day. The question was about the formula in post #1. Not real life.
what makes you think an online calculator uses different numbers/methods?
Junior here..Yeah, that was a good one. Glad you are being a sport about it and you didn't see me snicker the first time I read it. :lol:
Junior here..
I don't care if it does or not. You are evading the issue, and that issue is about the 'R' in the OP's first post. I think he made a valid observation.
Welcome to the forum! Not only are some of these guys a hoot, this is the best place I know of to learn about our trade.
the point is there is no adjustment required because of the physics of the system
you do not use R, you use Z (for AC systems)
Then why are three wires specified?
Because the effective inductance of the cable will be different if the current is unbalanced?
It should not change the skin effect term of the resistive component much though.
Toward the bottom of this page:
http://www.engineersedge.com/instrumentation/voltage_drop_calculations_10192.htm
""R" is the resistance per 1,000 ft. Use NEC Table 9 for AC wiring." From this page:
http://ecmweb.com/content/basics-calculating-voltage-drop
And in this PDF:
https://www.google.com/url?sa=t&rct...t7Tvh_zztl_0Qgrwg&sig2=cHNAw3HW1pLnjJTwITk0Kg
Then why are three wires specified?
So the NEC does not tell anyone to use chapter 9 right?
That's not the point. The point, at least to me, is the verbiage used. I'll use an online calculator and call it a day. The question was about the formula in post #1. Not real life. And someone thinks it matters, or it wouldn't be explicit as to 'three phase, three wires'. Why not just call it 60 Hz AC if it doesn't matter?
You lost me on that one, Bob.
3 ph in conduit at 60 Hz (most typical application)
those may be measured values since calculating the value may not be accurate or representative
those are the test conditions
what will change Xl based on conductor count?
Where does the NEC code tell us to use chapter 9 for voltage drop?
It's not the NEC. It's the requirements of the formula the OP presented. Not only is he the one that wants to use it, but as I pointed out, others use it as well.
And the point to me is the NEC does not tell us how to do voltage drop calculations so how can chapter 9 be looked at as right or wrong?
I know the OP didn't get his formula from the NEC, it just references the NEC.