jms53
- Clinton, In
This question has me stumped. Wanted to run it past you folks that have more code and calculation expertise than me. I understand everything except how the single phase 208 motor loads are added. Answer only shows value from 2 motors, and not 3. Any thoughts on why it's this way. It may have something to do with the way FLC's of all other motors on the same line are recognized. Any thoughts
Thanks for any help you may be able to provide.
[FONT="]Question:[/FONT][FONT="]8. • The motor feeder conductor size for three 15 hp, three-phase, 208V motors; three 3 hp, single-phase, 208V motors; and three 1 hp, single-phase, 115V motors will be _____.
[/FONT][FONT="](a) 2/0 AWG (b) 3/0 AWG (c) 4/0 AWG (d) 250 kcmil[/FONT]
[FONT="]
[/FONT]
[FONT="]
[/FONT]
[FONT="]Answer:[/FONT]
[FONT="]
[/FONT]
[FONT="]8. (c) 4/0 AWG[/FONT]
[FONT="][430.24(A) and Table 310.16][/FONT]
[FONT="]The feeder conductor must be sized not less than 125% of the largest motor FLC, plus 100% of the FLCs of all other motors on the same line. [/FONT]
[FONT="]Motor FLCs - Tables 430.248 and 430.250[/FONT]
[FONT="]15 hp, 208V, three-phase = 46.20A[/FONT]
[FONT="]3 hp, 208V, single-phase = 18.70A[/FONT]
[FONT="] 1 hp, 115V = 16A[/FONT]
[FONT="]
[/FONT]
[FONT="] [FONT="]L1 L2 L3[/FONT][/FONT]
[FONT="]3 - 15 hp, three-phase 46.2 46.2 46.2[/FONT]
[FONT="] 46.2 46.2 46.2[/FONT]
[FONT="]3 - 3 hp, 208V 18.7 18.7[/FONT]
[FONT="] 18.7 18.7 [/FONT]
[FONT="] 18.7 18.7[/FONT]
[FONT="]3 - 1 hp, 115V 16.0 16.0 16.0[/FONT]
[FONT="][FONT="]
[/FONT][/FONT]
[FONT="]Feeder conductors must not be less than: (46.20A x 1.25) + 46.20A + 46.20A + 18.70A + 18.70A + 16A = 203.55A[/FONT]
[FONT="]4/0 THHN is rated 230A at 75ºC[/FONT]
[FONT="] Note: 3/0 THHN is only rated for 200A at 75°C[/FONT]
[FONT="]
[/FONT]
[FONT="]
[/FONT]
[FONT="]
[/FONT]
[FONT="]
[/FONT]
[FONT="][FONT="]
[/FONT][/FONT]