The "ground" in each parallel set could be #2 AWG, per 250.102(C)(2)with 1/0 ground in each parallel set
The "ground" in each parallel set could be #2 AWG, per 250.102(C)(2)with 1/0 ground in each parallel set
isn't it 2/0 since the "equivalent area for parallel conductors" is 500MCM + 500MCM? or am i understanding this wrongThe "ground" in each parallel set could be #2 AWG, per 250.102(C)(2)
No, I would just ask him if the "minimum" wire size is enough. I wouldn't open another can of worms asking about non-linear loads.But that is something you may want to ask the AHJ since this issue is something they will be paying close attention to.
You do not need to size your conductors any larger than the protective device.yup. i think we're just gonna do this.
so with 500A mcb ahead, we must have wire sized for 625A (500A/0.8) since we have 4 current carrying conductors.
that means we'll need 2 parallel sets of 400MCM wire.
using 250.66 we'll need 2/0 ground on each set of the feeder.
sound about right?
It's #2 because the size of the conductors in each conduit is 250mcm.isn't it 2/0 since the "equivalent area for parallel conductors" is 500MCM + 500MCM? or am i understanding this wrong
this is copper btw
This would be you SSBJ.yup. i think we're just gonna do this.
so with 500A mcb ahead, we must have wire sized for 625A (500A/0.8) since we have 4 current carrying conductors.
that means we'll need 2 parallel sets of 400MCM wire.
using 250.66 we'll need 2/0 ground on each set of the feeder.
sound about right?
Understanding the correct verbage will help with correctly sizing that conductor.The "ground" in each parallel set could be #2 AWG, per 250.102(C)(2)
Since you going with two sets and have read 250.102 (C) (2).yup. i think we're just gonna do this.
so with 500A mcb ahead, we must have wire sized for 625A (500A/0.8) since we have 4 current carrying conductors.
that means we'll need 2 parallel sets of 400MCM wire.
using 250.66 we'll need 2/0 ground on each set of the feeder.
sound about right?
Over 3/0 through 350 cuYea I was leaning on the heavy side since I don't want to piss off the inspector anymore. But yes most loads are nonlinear.
So then I'll go with 2 sets of 250MCM wire with 1/0 ground in each parallel set
Thank you very much for the clarification. I understand now. 250.66 is meant for services but the "separately derived system" threw me off.This would be you SSBJ.
Size it according.
Understanding the correct verbage will help with correctly sizing that conductor.
Do not use 250.66 for an SSBJ
(Supply Side Bonding Jumper).
Since you going with two sets and have read 250.102 (C) (2).
You would size your SSBJ for each based on the ungrounded wire size using table 250.102 (C) (1).
Over 3/0 through 350 cu
Is a #2 cu.
If in two raceways.
If a Single race way then it would be sized for 500 (250*2) Mcm cu and the table says 1/0 CU.
This is where terminology helps. Sizing for an EGC will differ for parrelle conductors in separate race ways versus an SSBJ.
So try not to use the word ground when sizing or you will be lead astray. As there is no table for ground(the earth) in artical 250.
We usually do (2) sets of 4 #300kcmil cu and 1 #2 cu e.g. in 3"c ea for this scenario.yup. i think we're just gonna do this.
so with 500A mcb ahead, we must have wire sized for 625A (500A/0.8) since we have 4 current carrying conductors.
that means we'll need 2 parallel sets of 400MCM wire.
using 250.66 we'll need 2/0 ground on each set of the feeder.
sound about right?
Two sets of 300's is only 570 amps so that is too small if he needs 625 amps. Parallel 350's at 310 amps each (310+310=620) would also be too small so he's correct in saying that he needs 400's. There are no equipment grounds run with the secondary conductors. The conductors run in each parallel raceway would be SSBJ's.We usually do (2) sets of 4 #300kcmil cu and 1 #2 cu e.g. in 3"c ea for this scenario.
I went with 2 sets of 250s since the neutral is not considered a current carrying conductor.Two sets of 300's is only 570 amps so that is too small if he needs 625 amps. Parallel 350's at 310 amps each (310+310=620) would also be too small so he's correct in saying that he needs 400's. There are no equipment grounds run with the secondary conductors. The conductors run in each parallel raceway would be SSBJ's.
That works. It is extremely rare that the neutral ends up being a CCC on a transformer secondary.I went with 2 sets of 250s since the neutral is not considered a current carrying conductor.