That inspector has lost his mind
If indeed he ever had one?That inspector has lost his mind
First, there's no recognized procedure for conducting a "tug" test. Second, it's clear from the description that the inspector is applying force until he generates a failure.Every one is saying the inspector is wrong, I disagree if heavy cables can be pulled out they are loose. I teach my apprentices to pull the wire back and forth then retorque.
Even torquing relaxing and torquing 3 times how I was taught 40 years ago with my “arm strong” torque is not enough (notice each time the screw trend further) heavy gauge wires will burn off as they relax the pulling on the wires gets them to relax under the clamp so they are no longer tight.
As for the flex I would disagree with pulling on that but for the heavy gauge stranded as all heavy gauge is stranded the round conductors can stack with vibration they become loose and burn off causing all kinds of problems.
Yeah . . . I am wondering if there are some underlying mental health issues.If it was I bet I can tell you his name. That inspector is something.....
Sent you a PM.Yeah . . . I am wondering if there are some underlying mental health issues.
Have not met him yet, but I have 3 projects that have "problems" coming up to resolve for different contractors -- and this one is the common thread.
I have seen this and always wondered though never looked further.
Does that mean a “250in pound torque” is initially for the compression of the material, and they account for slacking so the final connection is not really “250 in pounds”
Plus if your using copper the compression going to be much different.
Seems unless they have a different value for copper along the the range of final torque value the material will end up at, torque is garbage!!
Unless like you said use crimp on. No one’s going to do that though for a small resi service though.
The clamping pressure actually comes from fastener stretch, which is approximately accomplished by tightening until the specified torque is achieved. When you see the plates with all the nuts'n'bolts that connect girders, the strength of the joint comes from the clamping pressure, not the bolts' shear strength.
I would imagine the relaxing that Paul mentioned in post #16 is taken into account when torques are specified for mechanical connections. Otherwise, we would be instructed to tighten in steps, the way we are when torquing cylinder head bolts when assembling engines (which I know also minimizes warping.).
That should be printed on my headstone some day. LMAOSure could use those spare parts I got rid of 3 months ago.
I did a tug test today. Obvious overheating on a starter lug. Couldn't loosen it enough to get fresh conductor and barely tighten enough to make it work for awhile. Maybe. Sure could use those spare parts I got rid of 3 months ago.
This Occurred in Mckinney. Apologies for the late reply. Been crazy busy like the rest of us!If it was I bet I can tell you his name. That inspector is something.....
Yep wearing a body cam next inspectionIn the future I would video all of his inspections.
Will do.@cbooker please keep us updated on the matter, thanks.
MckinneyThis is so bizarre. Had a solar crew member tell me that we had an inspector yanking (grab and pull) on feeder wires on a job site last week. And these were LIVE conductors. Is this Covid Brain Damage or what?
My hands GO-IN-MY-POCKETS on someone else's job site -- even if I am doing commissioning or inspection.
cbooker -- was this in Irving?
I don't happen to have the lug in my nonexistent inventory but I'm sure the local Siemens supplier has one on the shelf.Once the lugs are so hit they are discolored and the wire and lug are fused, the lug needs replaced.
Sent from my iPhone using Tapatalk