NEC Voltage Drop Calcs & Power Factor

Status
Not open for further replies.

shespuzzling

Member
Location
new york
Been putting together a voltage drop calculation spreadsheet based on the NEC tables and noticed something surprising. I though that the voltage drop in a circuit would always increase with decreasing power factor. That tends to be the case with larger wire sizes (3/0 and above) but is definitely not the case with smaller wires. These calculations were based on Chapter 9 Table 9, I could show my work if you want but taking the following parameters, the voltage drop is worst with unity pF:

A=50A
wire size=8awg
length=50
voltage=120
phase=1

Here are the percent voltage drops I got starting with pf=1, then .9, .8, .7, .6 ,......,.2

pf=1 - 3.24%
3.04%
2.76%
2.47%
2.17%
1.86%
1.55%
1.23%
pf=0.2 - 0.92%

This happens for all the wires up to 2/0. What gives? Is it just due to the impedances of smaller wires?
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
..I though that the voltage drop in a circuit would always increase with decreasing power factor..

My Tbl-9 calculator followed your results also - for purely resistive loads only. Very interesting, perhaps the engineers can explain this?

However, for inductive-motor loads adjusted per NEC 220.18(A), both Current and Voltage Drop increase with decreasing Power Factor, inversely proportional, as expected.
 