Normally, you size your wires according to the fuse before those wires. Except for drives (VFDs). NEC says that you have to size your wires according to the capacity of the drive times 1.25 (125%). (the drive's electical capacity, not the overload setting in the drive parameters!)
So, my Siemens G120X is specified with an input (LO mode) of 120A at 460V, my motor FLA is 110A. It can pull 110% for up to 60s at a time. So my formula for the wire ampacity is:
120A * 1.10 * 1.25 = 165A minimum.
Now, let's say I can buy the motor and the drive in bulk for a very good price and using the same motor+drive combination for various applications saves me a lot of money on spare parts in my warehouse. But in some of my applications this motor will be oversized and never run on more than 50%. I am allowed to do that.
Well, if my motor runs on 50% only, there is no need for a big fuse before the drive. (Siemens says for that drive the max fuse is 200A) 60A will be enough. So my fuse should be: 60 * 1.10 = 66A, let's do 80A. However, my wires still need to be sized for a 165A minimum (NEC!), because the capacity of the drive is what counts for the wires. But 165A wires after a 80A fuse makes no sense, does it?
Another typical scenario: customer calls: "need drive xy, production is down!" My Siemens supplier says: "xy has a lead time of three weeks, but we have yz on hand, which is one size bigger but will work with your motor". Then I say: "With yz the wires to the drive will be too small and need to be replaced (NEC) even though the motor will never pull more amps only because it has a bigger drive now."
So, my Siemens G120X is specified with an input (LO mode) of 120A at 460V, my motor FLA is 110A. It can pull 110% for up to 60s at a time. So my formula for the wire ampacity is:
120A * 1.10 * 1.25 = 165A minimum.
Now, let's say I can buy the motor and the drive in bulk for a very good price and using the same motor+drive combination for various applications saves me a lot of money on spare parts in my warehouse. But in some of my applications this motor will be oversized and never run on more than 50%. I am allowed to do that.
Well, if my motor runs on 50% only, there is no need for a big fuse before the drive. (Siemens says for that drive the max fuse is 200A) 60A will be enough. So my fuse should be: 60 * 1.10 = 66A, let's do 80A. However, my wires still need to be sized for a 165A minimum (NEC!), because the capacity of the drive is what counts for the wires. But 165A wires after a 80A fuse makes no sense, does it?
Another typical scenario: customer calls: "need drive xy, production is down!" My Siemens supplier says: "xy has a lead time of three weeks, but we have yz on hand, which is one size bigger but will work with your motor". Then I say: "With yz the wires to the drive will be too small and need to be replaced (NEC) even though the motor will never pull more amps only because it has a bigger drive now."