Does the wiring to my nonincendive device have to be installed in accordance with 501.10(B)(3)?
501.10(B) addresses wiring requirements and permits the use of conventional junction boxes in 501.10(B)(4) provided 501.105(B)(1), 501.115(B)(1), or 501.150(B)(1) don’t apply. In my case, because the device is nonincendive, the three (3) referenced sections don’t apply.
The device has been tested and approved to ISA 12.12.01 for nonincendive devices. Under the heading “Purpose” in the ISA standard it states:
Because 501.10(B)(3)) starts off with “Nonincendive field wiring shall be permitted…”, and based on the above highlighted section, I’m assuming I don’t have to install the wiring as “nonincendive” per 501.10(B)(3).
Am I missing anything?
501.10(B) addresses wiring requirements and permits the use of conventional junction boxes in 501.10(B)(4) provided 501.105(B)(1), 501.115(B)(1), or 501.150(B)(1) don’t apply. In my case, because the device is nonincendive, the three (3) referenced sections don’t apply.
The device has been tested and approved to ISA 12.12.01 for nonincendive devices. Under the heading “Purpose” in the ISA standard it states:
The purpose of this standard is to provide minimum requirements for the design, construction, and marking of electrical equipment or parts of such equipment for use in Class I and Class II, Division 2 and Class III, Divisions 1 and 2 hazardous (classified) locations. This equipment, in normal operation, is not capable of causing ignition of the surrounding atmosphere under the conditions prescribed in this standard, although the equipment may contain electronic components that operate at incendive levels and may also have field wiring that is incendive. In addition, it is the intent of this document to establish uniformity in test methods for determining the suitability of the equipment and associated circuits and components as they relate to potential ignition of a specific flammable gas or vapour-in-air mixture, combustible dust, easily ignitible fibers, or flyings.
Because 501.10(B)(3)) starts off with “Nonincendive field wiring shall be permitted…”, and based on the above highlighted section, I’m assuming I don’t have to install the wiring as “nonincendive” per 501.10(B)(3).
Am I missing anything?