I want to use NEC .. I know that NEC is based on 60Hz (USA)..but all motors I have (50Hz ,380V) ..
What should I do ?
There are two terms that apply when talking about the current of a motor in the NEC. They are the FLC value, and the FLA value. These terms really stand for "full load current" and "full load amperes" which sound like interchangeable synonyms. But the NEC makes an important distinction.
A good way to remember it, is pretend the terms stand for the following:
FLC = "full load code"
FLA = "full load actual"
FLC are tabulated values of current in the NEC to correspond to typical motors with a given horsepower rating of the mechanical output power. Usually this is an upper limit to the current of the motor, so it allows you to design your motor branch circuit in a brand-agnostic manner. In other words, it doesn't matter what specific motor you put in that position in the circuit, as long as it is a motor with the horsepower and other specs as specified.
FLA values by contrast come from the motor's own nameplate or manufacturer's datasheet, and reflect the efficiency and other details of the specific make/model of inverter, at the voltage rating selected. This is the current that it draws according to the way the product test results.
If you have a motor that isn't built for grids governed by the NEC, there is no table of FLC values for motors built for foreign grids. You can get a general trend from the theory that Winnie provided. You will still have the FLA value from the specific motor datasheet, which is what you should ultimately consult for planning the circuit. Some motors allow you to adjust taps on the windings, to adapt it one of several different grid voltage/frequency combinations. There may be a change in the rating of the mechanical output power/torque/speed, due to a change in the voltage and/or frequency