A ad42581 New member Location Pennsylvania Mar 28, 2003 #1 Does Class 2 Division 2 Group G location require explosion proof motors and any special NEMA enclosures?
Does Class 2 Division 2 Group G location require explosion proof motors and any special NEMA enclosures?
rick5280 Senior Member Mar 28, 2003 #2 Re: NEC See Article 502 of the NEC. Motors are not required to be explosion-proof, but could be used in this area. (See 502.8(B)) Box shall be dust-tight. (See 502.4(B)(4)) Rick
Re: NEC See Article 502 of the NEC. Motors are not required to be explosion-proof, but could be used in this area. (See 502.8(B)) Box shall be dust-tight. (See 502.4(B)(4)) Rick
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Mar 28, 2003 #3 Re: NEC See 502.8(B) for the motor. In general it must be of the totally enclosed type and have a maximum full-load external temperature no higher than that listed in Table 500.8(C)(2). Don
Re: NEC See 502.8(B) for the motor. In general it must be of the totally enclosed type and have a maximum full-load external temperature no higher than that listed in Table 500.8(C)(2). Don