Is there a standard for the number of Romex cables that can be feed through a given size Romex clamp to enter a circuit breaker box?
 
Re: NEC

I apprenticed back when, and out where, what limited the number of cables a connector could handle was the inside diameter of the throat and whether I could squeeze one more in. . . ;)

The two screw metal clamp
05103.gif

was what I had to work with.

At some point, I learned that none of them were listed for more than one cable. That has changed somewhat. . .but the difficult thing for me was I was comfortable with the old way and didn't want to learn new tricks.
 
Re: NEC

Direct from Arlington's site.
This is for a #841, typical 2-screw zinc NM connector:

1-14/2 & 1-14/3
1-14/2 to 10/2
1-14/2 & 1-12/3
1-14/3 to 10/3
1-12/2 & 1-14/3
2-14/2 to 10/2
1-12/2 & 1-12/3
1-14/2 & 1-12/2
2-14/2 & 1-14/3
1-14/2 & 1-10/2
2-14/2 & 1-12/3
1-12/2 & 1-10/2
3-14/2
 