B bmiller212 New member Jun 12, 2008 #1 NEC 240-21, Ten Foot Tap Rule - Can the Taps be disconnects and if so can it be applied to NEC 230-71, Maximum Number of Dissconnects?
NEC 240-21, Ten Foot Tap Rule - Can the Taps be disconnects and if so can it be applied to NEC 230-71, Maximum Number of Dissconnects?
iwire Moderator Staff member Location Massachusetts Jun 12, 2008 #2 bmiller212 said: NEC 240-21, Ten Foot Tap Rule - Can the Taps be disconnects and if so can it be applied to NEC 230-71, Maximum Number of Dissconnects? Click to expand... If your dealing with 230 then 240.21 has no relevance. 230.71 has to due with service conductors not feeders. 240.21 Is about tapping feeders.
bmiller212 said: NEC 240-21, Ten Foot Tap Rule - Can the Taps be disconnects and if so can it be applied to NEC 230-71, Maximum Number of Dissconnects? Click to expand... If your dealing with 230 then 240.21 has no relevance. 230.71 has to due with service conductors not feeders. 240.21 Is about tapping feeders.