NEC 240-21, Ten Foot Tap Rule - Can the Taps be disconnects and if so can it be applied to NEC 230-71, Maximum Number of Dissconnects?
 
bmiller212 said:
NEC 240-21, Ten Foot Tap Rule - Can the Taps be disconnects and if so can it be applied to NEC 230-71, Maximum Number of Dissconnects?

If your dealing with 230 then 240.21 has no relevance.

230.71 has to due with service conductors not feeders. 240.21 Is about tapping feeders.
 