NEC

Status
Not open for further replies.

atbenson

Member
I have a 320 meter base and off of it 2 200 amp disconnects. Off of each disconnect I have 2 ground rods. For a total of 4 ground rods. Each set of ground rods is connected to #6 bare wire. Do I have to have ground rods connected from disconnect through ground rods through other set of ground rods back to other disconnect. I just failed an inspection because I didn't. But I have done this before and always passed.
 
Re: NEC

It sounds like you have two separate services, perhaps to two different buildings. I think each disconnect represents a separate entity, and that each should be handled separately. It does not matter if there is another service disconnect in the area, and the fact that two disconnects come from the same meter does not change the situation.

Can you get the Inspector to cite an NEC article as the basis for failing your installation?
 
Re: NEC

I don't see that you would need 4 rods, 2 would suffice. As for the loop, if you are in NY state, then I would say YES. We are required (at least in my area) if using rods, to go from grounding terminal in disconnect to first rod, then to second rod, then back to grounding terminal all with one unbroken conductor.
This is under the presumption that this is for one building being served. Edit to clarify that.

[ December 20, 2005, 10:39 AM: Message edited by: BruceH ]
 
Re: NEC

You are only required to ground A service once. 250.24(A)(1) specifies where this grounding can be accomplished. Otherwise, you are exceeding the requirements of the NEC.
 
Re: NEC

Originally posted by BruceH:We are required (at least in my area) if using rods, to go from grounding terminal in disconnect to first rod, then to second rod, then back to grounding terminal all with one unbroken conductor.
I think the point here is that the OP is being required to go from one service to its pair of ground rods, and then to the pair of ground rods for the other service, and then back to the second service. I believe that is not required, and I think it might even be the wrong thing to do. I would not want my house's electrical system to be impacted by any kind of fault in my neighbor's system. If there is dirt separating his ground rods from mine, then I would consider that adequate isolation. If his ground rods are bonded to my ground rods, our systems would no be independent. I'm not sure if anything bad could ever happen, but I am sure I would not like the situation.
 
Re: NEC

I second Bryan's question.

As far as what the inspector wants, I know that there is nothing prohibiting these loops, but I see it as unnecessary parallel neutral current paths.

Roger
 
Re: NEC

It sounds like you have two separate services
charlie b, you are obviously far wiser than I am, and I try not to question you, but, in this case, I read that we may be talking about ONE service to a 320 amp socket and then two disconnects (common in this area). I posted a similair question at
http://www.mikeholt.com/codeforum/ultimatebb.php?ubb=get_topic;f=11;t=008947.
In this case, I see no reason for 4 ground rods (if the disconnects are grouped and not on seperate buildings). As questioned in my earlier post, to me, it is questionable if the 2nd disconnect even needs GE's if the 1st one is sized adequately for the service.
I would say if you had multiple ground rods, as grounding electrodes they would need to be bonded together, but one might take the stand that they are since both have GEC's back to the service.
I would think, two rods, with the GEC from one service disconnect would actually meet NEC. A GEC from the 2nd disconnect to the same rods might be in order.
 
Re: NEC

Originally posted by bphgravity:
Why not just terminate the GEC to the grounded conductor in the meter enclosure?
This practice is prohibited by two of the pocos in my area. Sounds like we need all the details from the OP.
 
Re: NEC

We are required to ground to the meter base and that is it .poco says no way will they hook up if attached at an inaccesabile panel (inside).
Now a gas bond can be from the meter ground or tagged off the panel.But there has to be a seperate connection for that
 
Re: NEC

Yeah, I know it varies with poco's. I beleive the reason they mention is to make it so you don't need to cut their locks off if you ever need access to the gec termination.
 
Re: NEC

I recently did a similar service: 320a base and two 200a disconnects feeding two ML panels via SER. I ran a single, unbroken #6 from rod A, inside into disconnect A (bent into a U into lug), back out, into to dosconnect B, back out, and back outside to rod B.

It sounds to me that the simple fix for the original question would be to inter-connect the closer rod of each pair with a #6 with separate clamps. Rods are supposed to be tied together.

Originally posted by allenwayne:
We are required to ground to the meter base and that is it .poco says no way will they hook up if attached at an inaccesabile panel (inside).
That's funny: we can't land the GEC in the meter because it's inaccessible. I wish we could; it's the ideal point, since it's already outside.

[ December 21, 2005, 12:10 AM: Message edited by: LarryFine ]
 
Re: NEC

Seems to me that 250.24(B) is written for this exact scenario:

(B) Grounded Conductor Brought to Service Equipment.
Where an ac system operating at less than 1000 volts is
grounded at any point, the grounded conductor(s) shall be
run to each service disconnecting means and shall be
bonded to each disconnecting means enclosure. The
grounded conductor(s) shall be installed in accordance with
250.24(B)(1) through (B)(3).

I agree with Bruce, if these disconnects feed the same building you only need the 2 rods. As far as the loop back to the grounding terminal, I've never heard of that requirement out here in the west.
 
Re: NEC

Bryan S, are you confusing the grounded conductor with the grounding conductor, or in this case, the grounding electrode conductor? The loop I mentioned is required where I live, it's not an nec requirement.
 
Re: NEC

I still question why an inspector or anyone would want to intentionally create these circulating currents between the Grounded Conductor and the Grounding Electrode Conductor.

groundrodloop.jpg


Roger
 
Re: NEC

I'd take back two of the ground rods. It really sounds like they're on the same building.

I'd limit the problem Roger described by installing a busbar immediately below the disconnects, and then pull the GEC for the ground rod from there, and then attach the bonding jumper for the second rod to the first.

1100203955_4.jpg
 
Re: NEC

Bravo George, that is one way to eliminate the loop, but there is nothing prohibiting it either.

IMO, if per the NEC, we can legally, (not sensibly) and in some cases even be required by inspectors to install a ring that will divide current proportionately between the grounded and grounding conductors, it would also be legal to use a ring in any circuit, or more specifically, any circuit conductor. :)

Roger

[ December 21, 2005, 10:20 PM: Message edited by: roger ]
 
Re: NEC

Take a look at 250.58 and 250.64(D)

Using the illustration in George's post, you would only need one more conductor to the second service disconnect from the detail below the panel.

BTW: Roger nice illustration :cool:

[ December 21, 2005, 11:39 PM: Message edited by: pierre ]
 