Are there any min front access working clearances required for a cabinet that is purely fiber optic?


Sent from my iPhone using Tapatalk
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Does it have energized metal parts that could accidentally be touched by someone working on the fiber?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Working clearance is required for components that are likely to need maintenance while energized. It seems to me that your fiber optic cabinet does not fit that criterion.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Working clearance is required for components that are likely to need maintenance while energized. It seems to me that your fiber optic cabinet does not fit that criterion.

Agreed - would minimum general access apply?
Such as 30”deep and 30” wide—
Or zero minimum?


Sent from my iPhone using Tapatalk
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The issue is that the first row of requirements in Table 110.26(A)(1) starts at ZERO...that would seem to include fiber that has no voltage on it
:D ;)
 

ruxton.stanislaw

Senior Member
Location
Arkansas
Occupation
Laboratory Engineer
Keep in mind that fiber in longer range installations must be respected. The light energy some transfer are capable of instantly blinding, burning, starting fires etc.
 