NEC2017's 690.11 section now has an exception to not require AFCI on ground-mount systems, provided certain conditions are met.
This exception seems to systematically exclude what I'd do by default on a ground mount system, which is wiring underground in PVC conduit. Possibly unintentionally, it just excludes this by omission. Or this may be intentional for reasons I don't understand. Yet it includes direct burial, which is less safe than wire in a PVC conduit. Direct burial is subject to physical damage from underground rock movement, while PVC provides a physical barrier against this, as well as the ability to future-proof and replace wire without re-digging.
I'd like to ask if wire underground in PVC is part of the condition of "direct buried" for this exception. And if it isn't, I'd like to ask if PVC underground was intentionally or unintentionally excluded from this exception, and why.
- The system & its wiring are not on or in a building
- The wiring is either
- Direct buried
- In a metal raceway
- In an enclosed metal cable tray
This exception seems to systematically exclude what I'd do by default on a ground mount system, which is wiring underground in PVC conduit. Possibly unintentionally, it just excludes this by omission. Or this may be intentional for reasons I don't understand. Yet it includes direct burial, which is less safe than wire in a PVC conduit. Direct burial is subject to physical damage from underground rock movement, while PVC provides a physical barrier against this, as well as the ability to future-proof and replace wire without re-digging.
I'd like to ask if wire underground in PVC is part of the condition of "direct buried" for this exception. And if it isn't, I'd like to ask if PVC underground was intentionally or unintentionally excluded from this exception, and why.