I'm helping my BiL.

He's trying to hook up a 3P A/C and the L1,L2,L3 aren't clearly marked.

From the picture he sent me here I am guessing that the lugs on the top of the right hand contactor are where his wires are to go. He'll double check with the wiring diagram when he gets back there but would like some additional educated guesses.

The unit is a York ZH150N15 if you are familiar with York.
 

norcal

Senior Member
My guess also that the line leads would go on the contactor on the right, otherwise you have multiple conductors under 1 lug, factory wiring as shown does not count IMO. What does the wiring diagram say?

4380059853_96bd3bbb30.jpg
 

JES2727

Senior Member
Location
NJ
Yes, I would agree that the supply wiring is to terminate on the lugs on the top of the contactor on the right.
 

220/221

Senior Member
Location
AZ
L1,L2,L3 aren't clearly marked.

Thery are surely marked on the diagram.

It looks like the 3 open lugs would be the obvious choice.


When he turn the unit on, have him listen closely to it. A 3phse compressor makes a lot of noise when it runs backwards :roll: A few seconds won't kill it but it won't help it any.
 

JLCELEC

Member
Location
nj
I agree they should be wired to the contactor on the right. My guess is that this is a start run contact for a motor of some sort.
 

e57

Senior Member
I would read the schematic on the door and identify the component where they would go... Then again - I'm an 'lectrician... And depending on your point of veiw - a qualified people.
 

ceb58

Senior Member
Location
Raeford, NC
From what I've heard, AC compressors aren't phase-direction-sensitive, although ancillary equipment may be.

Scroll compressors usually dont care on rotation. A rotary compressor is directionally sensitive. But as you said the ancillary equipment may be.
 

R Bob

Senior Member
Location
Chantilly, VA
From what I've heard, AC compressors aren't phase-direction-sensitive, although ancillary equipment may be.

For the most part, and in this application, that is true.
A more critical check of phase rotation is to make sure the blower and condenser fans are turning in the correct direction.
 

R Bob

Senior Member
Location
Chantilly, VA
Scroll compressors usually dont care on rotation. A rotary compressor is directionally sensitive. But as you said the ancillary equipment may be.

Scroll compressors are rotation sensitive.
Most of the large ones have phase monitoring and lockout, otherwise, the only reliable way to postively confirm rotation is to make sure that the suction pressure is dropping and the discharge pressure is increasing on start up.
 