oops I meant a disconnect not a GES?
Yes, 225.32, Exception Nos. 3 and 4.
oops I meant a disconnect not a GES?
By the NECs definition of structure, there is no such thing as a detached structure where the NEC is relevant
A structure is 'that which is built or constructed'. Wiring is built or constructed. If I construct a building with some wires underground to a pole, I have a single structure, since the building and the pole are continuously connected by a constructed path.If I have two separate structures and I run wires between them, I have rendered them a single structure.
-Jon
I agree,
With which part?
Because while I think winnie's 'no separate structure theory' is interesting I have no doubt the CMPs will not agree with it.
By the NECs definition of structure, there is no such thing as a detached structure where the NEC is relevant
A structure is 'that which is built or constructed'. Wiring is built or constructed. If I construct a building with some wires underground to a pole, I have a single structure, since the building and the pole are continuously connected by a constructed path.If I have two separate structures and I run wires between them, I have rendered them a single structure.
-Jon
Because while I think winnie's 'no separate structure theory' is interesting I have no doubt the CMPs will not agree with it.
I believe that as worded the current definition of detached structure neither agrees with nor clarifies the common understanding of the term.
I tend to agree with the structure concept but that in itself creates other issues.
Let's look at a septic pump setup. Many of these units require 240v for the pump and 120v for the alarm. In some systems the alarm is tied to one leg of the pump-- problem-- yes. Since the 2008 we now have to have a dp breaker installed which would trip out the alarm on a short circuit or ground fault on the pump. Damn the alarm won't work. This makes this install illegal, at least around here.
Now run two circuits - a 240v circuit for the pump and a 120v circuit for the alarm. Problem again-- 225.30 unless one of the special conditions would apply (I didn't think it would). So if it's a structure, which I say yes to, then there is no legitimate way to wire the septic pump system.
I believe there must be an answer somewhere but as the NEC is written there isn't much that wouldn't qualify as a structure if it is detached from the building serving it. What is the intent-- who knows.
If it is UL listed and the mfg. instructions require two circuits,which all I have seen do I don't have a problem with it, be it a double pole and a single or two single pole breakers.
True.The definition of structure could use a little more thought.
We are going to install a new outdoor MLO subpanel to a conrete pole. It will get fed from a 208/120v 3 phase panel. The new panel will have 3 breakers in it serving a camera and lighting. Since it is not in a building or a structure, do we need to install a ground rod for this new subpanel?