Wow I completely spaced the lengths. Sorry for that. The #2 is about 380' and the 1/0 is about 550'.
i'm assumiing you don't have tugging stuff.....
buy yourself a spool of mule tape. it comes in different strengths.
buy a spool of 3000# test. you can get it cheaper on ebay.
buy a pail of pull string, and a mouse for the size pipe you have in the ground.
use a strong shop vacuum to suck the mouse in, and get a string in the pipe.
use that string to pull in the mule tape. the mule tape will not cut plastic pipe,
is very low friction, and can be used to pull directly. 3,000# test is enough.
it has every foot marked, so you can get an accurate wire measurement.
it is disposable, and a spool of the stuff is wonderful to have around.
did i mention i like mule tape?
get the mule tape in, get your measurement, order your wire cut, on separate
spools.
get a stick of 2" rigid. use it for an axle. put all the spools on the rigid, with
the wire coming off the top. i'm assuming this is an industrial situation, so
borrow a forklift, set the forks wide enough for two or three of the spools,
and put the other two spools outside of the forks. make sure there are no
tails of wire sticking out the sides of the spools, cut them off flush. place a
3" coupling in between each spool, and forks as well, to keep them from chafing.
i also use couplings on the outside of the reels, with kant-twist
clamps, to keep the outside spools from walking, otherwise the pipe will flex
and they'll walk off the pipe.
use a pair of c clamps on the forks, to capture the axle, so it doesn't walk.
pick this up, and position it so the wire will feed off the tops of the reels,
down into the pipe.
if your supplier uses webco reels, get it on webco's. put in the axle the
same, and get it up in the air. webco reels have a locking pin that holds
all the spools together, so the wire can be wound on at the supply house.
make sure you pull the pin out BEFORE you start the pull. i had a crew working
for me once that didn't, and the 4/0 turned the 500's faster, and the whole
thing got balled up.... don't even ask how long it took to fix, with 2,000' of
500 mcm at stake.
make up the pulling head. if you don't have hardware, like socks or cable
grips, you can make up a basket from tie wire, or skin back the wire for
2', take two strands from each side of each wire, cut the rest off, and
make up a pulling head.. use a swivel. buy one if you have to, or pm
me, and i'll lend you one... i have half a dozen.
there is wire insulation available that does not require soap. use it.
it's wonderful. use it. dump a quart of soap down the pipe anyway.
get a maxis 3000# tugger. rent it, whatever. set the tugger up to pull
out enough cable to make up without re rigging to pull more.
wires up in the air, soaps in the pipe, spacers between spools. take up the
slack, get the head in the pipe, and pull it. it should feed by itself. if you rig
it right.
it should take longer to set up the pull than to pull it.
working by myself, i've pulled 4 500 mcm copper and a ground 300', thru 4
90's, without help, using the above setup. took two hours to set up, and
half an hour to pull.
if you've got any questions, pm me.....
have fun.
randy