Re: Need code referance ?
For single circuits or a multiwire circuit one or more single pole switch's are allowed as the disconnect as long as it is rated for the circuit, and it disconnects all ungrounded conductors that enter the building.
Keep I'm mind that for the purpose of this a multiwire circuit can be considered a single circuit as said in 225.30
[ October 28, 2005, 10:01 PM: Message edited by: hurk27 ]
For single circuits or a multiwire circuit one or more single pole switch's are allowed as the disconnect as long as it is rated for the circuit, and it disconnects all ungrounded conductors that enter the building.
Keep I'm mind that for the purpose of this a multiwire circuit can be considered a single circuit as said in 225.30
225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.