cgamad550
Member
- Location
- United States
- Occupation
- Apprentice
I have a Question that I'm hoping you can help answer for me.
I recently purchased a property and at the service entrance. I have 2 copper wires coming from the EGC. One goes up top and is attached at the weather head to the neutral/ground coming in from the lines coming from the transformer, the other is going up into the meter can.
Is this properly grounded? There no ground wire in the service panel attached to the ground bar but the neutrals and grounds are bonded with the bonding screw.
We have issues with frequent power surges and I have installed a Square D HEPD80 SPD device. But someone told me if there's no EGC connected to the service panel itself that the SPD won't actually work. Is this correct?
Or do I need to install 2 ground rods and connect an EGC directly into the service Panel.
If you could please help me with this it would be greatly appreciated.
I recently purchased a property and at the service entrance. I have 2 copper wires coming from the EGC. One goes up top and is attached at the weather head to the neutral/ground coming in from the lines coming from the transformer, the other is going up into the meter can.
Is this properly grounded? There no ground wire in the service panel attached to the ground bar but the neutrals and grounds are bonded with the bonding screw.
We have issues with frequent power surges and I have installed a Square D HEPD80 SPD device. But someone told me if there's no EGC connected to the service panel itself that the SPD won't actually work. Is this correct?
Or do I need to install 2 ground rods and connect an EGC directly into the service Panel.
If you could please help me with this it would be greatly appreciated.