RBGS
- Boston, MA
I need some help with a Material List. I’m installing a new Meter, SE cable and a 200A Panel for a House in Massachusetts. May you guys verify my material list, and add, edit, or provide any suggestions?
Service drop to meter socket
(100ft) 2/0 Cu THHN or 100' 4/0 AL from service drop to meter terminals
(4) 2" PVC clips for the pipe on the side of the house
(1) 2" PVC Male connector
(1) 200amp Meter socket with 2" hub
Meter to panel Can be done straight from the back or out of bottom of meter socket using an LB...I'll use LB to get to basement sill
(1) 2" LB
(2) Short piece of 2" PVC
(1) 2" 90 degree
(1) 2" 45 elbow
(1) 2" PVC Male connector LN
(30ft) 2/0 Cu THHN
(1) 2" offset nipple
(4) 2" couplings
(2) 2" bushings
Panel including water ground
(1) 200 Amp 40 circuit panel with main breaker
(1) 30 amp breaker
(10) 15 amp breakers
(1-box) Romex Connectors
(1) Ground bar
1/2" connector for water ground
(50ft) #4 Cu to get to water ground
(2) water pipe clamps.
(1)1900 box
(1)Mulberry cover
(1)TR GFCI
(1) Offset nipple
Miscellaneous:
(1) Backer board
(3) Barrel splices
(2) Mastic Pads
(2) Silicone
(2) Duct seal
Did I forget anything? Please edit, add, or provide any suggestions!
Thank you!
(1) 2" LB
(1) 2" 90 degree
(1) 2" 45 elbow
(30ft) 2/0 Cu THHN
(4) 2" couplings
(2) 2" bushings
(1) 30 amp breaker
(1) Ground bar
(1)1900 box
(1)Mulberry cover
(1)TR GFCI
(1) Offset nipple
Miscellaneous:
(1) Backer board
(3) Barrel splices
(2) Mastic Pads
(2) Silicone
(2) Duct seal
Thank you!