I need help answering my conduit fill test I need help pasting this text ...............................
 
Last edited by a moderator:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

You'll find that we won't simply answer questions like this, but we will encourage you to try to answer them yourself, and we'll gladly guide you. You know, the proverbial fish. 🐟
 

TwoBlocked

Senior Member
Location
Bradford County, PA
Occupation
Industrial Electrician
I need help answering my conduit fill test I need help pasting this text ...............................
Myself, I'd be more willing to help someone trying to understand something, than someone trying to answer questions from a test. There is a difference.

So what part of determining conduit fill do you want to understand better?
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
A common error in this calculation is using the information in Table 8 as the conductor cross sectional area. Table 8 shows the cross sectional area of only the metal in the conductor; you need to make the calculation using the total area of the conductor including the insulation. Obviously, the result will be different for different conductor types. Perhaps ironically, the result isn't different for copper vs aluminum conductors.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
A common error in this calculation is using the information in Table 8 as the conductor cross sectional area. Table 8 shows the cross sectional area of only the metal in the conductor; you need to make the calculation using the total area of the conductor including the insulation. Obviously, the result will be different for different conductor types. Perhaps ironically, the result isn't different for copper vs aluminum conductors.
Table 5 is used for this purpose, or where the cable or conductor is not found in that table, you use the manufacturer's data.
 
Location
Texas
Occupation
electrical Code instructor and mentor
2023 NEC
Use Chapter 9, Tables 5 and the Approximate Area Column to determine the square inch(in.2 area of a conductor.
Use this table when you have various sizes of conductors in a raceway.

If all conductors are the same size and type of insulation you can get a quicker answer from Informative Annex C (over in back of Code book)
For fixture wires ,too.
See the first page of IA of C for a table with various types of raceways.
Watch out for the asterick * see the foot note.
Then you use Table(s) 4 found in Chapter 9.
Typically, you'll use the Over 2 Wires at a 40 % fill and the in2 column to get the total square inch areas.
For nipple fill you use the 60% Column. A conduit nipple is 24 inches or less.
A raceway is any thing beyond 24 inches, Chapter 9 Table 1 and Note(s) (4) for tubing nipples.

Now go pass that test and let us know.